Question about fault control in 30F5015
stoyanoff
PostPosted: Fri Jun 07, 2013 6:58 am     Reply with quote
Hi! I have a problem with 1 30F5015. I`m controlling IGBT bridge with it and I have a protection connected to FAULTA pin. So when I`m starting the bridge the big current consumption in the begging is disturbing the fault pin and activates the interrupt. In the INT_FAULTA I`m stopping the PWM outputs. So I need to make a simple software protection to avoid this ENP. BUT if I enter in this interrupt the fault control is stopping the pwm outputs immediately - Cycle-by-Cycle mode(30F5015 datasheet page 105). So could you give me an advice how to deal with this problem?
Thanks!
Mike Walne
PostPosted: Fri Jun 07, 2013 8:45 am     Reply with quote
Soft start.
Mike
stoyanoff
PostPosted: Fri Jun 07, 2013 9:53 am     Reply with quote
Yes! But before I start the bridge the filter caps are charged to voltage above work values. So on first pwm pulses I`m decreasing the duration the dv/dt is too big and it creates a powerful EMP. As far as I remember in the older version in 18F4431 the fault pin is waiting for few cycles and if the port is low again it triggers the interrupt.
PostPosted: Fri Jun 07, 2013 11:17 am     Reply with quote
Generally a current limit fault, _wants_ to trigger if the current exceeds the safe level, without exception. You say you are 'decreasing the duration'. Is it the minimum it can be?. The normal practice would be to program the shortest pulse possible, and send this for a number of cycles before starting the PWM control.
If the fault is on 'per cycle', you will get a truncated pulse from the PWM, which will stop where the current limit exceeds, which is ideal for start up.
Fault doesn't delay on the 4431.
stoyanoff
PostPosted: Sat Jun 08, 2013 12:07 pm     Reply with quote
Is there a way to trigger only the Fault interrupt
enable_interrupt(INT_FAULTA);
without triggering the output suppress interrupts
set_motor_unit(1,4,MPWM_ENABLE | MPWM_INDEPENDENT|MPWM_FAULTA_LI_HI,100,100);
Thanks!
PostPosted: Sat Jun 08, 2013 12:41 pm     Reply with quote
These are not separate.
The fault interrupt, triggers the outputs to go to a safe condition.
No separate 'interrupt'.
You can turn off the switching to the safe condition in the PWM setup. and effectively use the fault input as a 'normal' interrupt, but then your driver risks overloading.
stoyanoff
PostPosted: Sun Jun 09, 2013 4:34 am     Reply with quote
OK! I want to suppress my EMP disturbance by adding a small delay (1us) and checking again the fault input. If it`s low again -starting the protection. There is one detail - how can I check if the pwm counter is in active state or is inactive?
Thanks!
notbad
PostPosted: Sun Jun 09, 2013 4:04 pm     Reply with quote
are you having a problem with charging of capacitors?
or the current surge when starting the motor?
if you increase the duty cycle slowly from zero there should be no problem.
stoyanoff
PostPosted: Sun Jun 09, 2013 11:03 pm     Reply with quote
I've tried this - no success! I added duty cycle correction depending on the voltage on the bridge - no effect. So I need to know how can I check if the pwm pulse is in active state (1) or is in inactive state(0) till it's counting?
Thanks!
notbad
PostPosted: Mon Jun 10, 2013 3:22 am     Reply with quote
You can check if timer value is greater than ccpr.
But I think you're going in wrong direction.
Are you sure your circuitry for current threshold is correct?
PostPosted: Mon Jun 10, 2013 3:30 am     Reply with quote
Agreed.
I'd actually suspect something really dangerous is going on (like both sides of the bridge switching on at once), and as such the fault input is saving things....
