Can You help me about read_adc.
sraiderk
PostPosted: Thu Feb 24, 2005 9:09 am     Reply with quote
I want to learn the difference of the using optional parameter of read_adc.
is there a any time difference the reading the analog value using
read_adc() or
read_adc(ADC_READ_ONLY )
and also how many time delay needed between two different channel reading?
set_adc_channel(0)
delay_us(40); // is it ok? or 1us ok?
x=read_adc();
set_adc_channel(1)
delay_us(40);
y=read_adc();
Could you help me about this topic
DragonPIC
PostPosted: Thu Feb 24, 2005 11:04 am     Reply with quote
read_adc() is default to ADC_START_AND_READ. This reads and waits in the called function until a measurement is complete (is determined by the GO/~DONE bit of ADCON0 register.
read_adc(ADC_READ_ONLY ) will read what is in the ADRESH/L registers. This is usually used with read_adc(ADC_START_ONLY ) so can do other important things while waiting for the ADC to finish it's measurement.
10us delay is recommended in CCS manual. (Check the datasheet for the PIC you are using)
-Matt
PostPosted: Fri Feb 25, 2005 4:26 am     Reply with quote
The 'point' about the time delay needed after changing channels, is that it depends on a whole lot of parameters. Inside the chip, the ADC input, is effectively a capacitor, which has to charge to the new voltage. There is a series resistor inside the chip. Both the value of the capacitor and resistor, change slightly with different chip versions. The '10uSec' figure, that comes in several of the data sheets, is the time needed to get within 0.5 bit, on the 10bit ADC, using the full accuracy of the ADC, with a voltage source that has changed from one limit of the ADC to the other, and has a source impedance below typically about 2.5K ohms.
Now (for instance), if you are prepared to accept only 8bit accuracy, you only need to charge for 1/4 this time. Also if your source impedance is lower than the recommended figure, the charge time will improve a little (though the internal resistance in the chip then becomes the limiting factor).
Now on the parameters, another user has given 'what' they mean, but let me give an example of how these could be used. Suppose you want to sample four ADC channels, and have each reading updating at 1000 times a second. The 'simple' approach, would be to have a timer interrupt occuring every 1000th second, and in the timer have something like:
    static int8 count=0; //must be static so 'count' is retained
    count = (count+1) % 4; //count through 0..3 and start again
    set_adc_channel(count);
    delay_us(10);   //wait for capacitor to charge
    adval[count]=read_adc();  //take the reading - time will depend on
                           //the clock rate chosen.
The problem' with this, is that you will be inside the interrupt for a relatively long time. The reeading itself, make take perhaps 16uSec, so the 'core' of the change channel and read code, is probably going to run to perhaps 30uSec or more. If the chip is doing a lot of other work (perhaps serial etc.), this may be undesirable. Also a slightly longer charge time might well be preferred.
The alternative, would be to have an interrupt at 4* the speed (every 250uSec), and code with something like:
    static int count=0,state=0;
    switch (state) {
    case 0:
               state=1;
    case 1:
               state=2;
               read_adc(ADC_START_ONLY);
    case 2:
               state=3;
               adval[count]=read_ADC(ADC_READ_ONLY);
    case 3:
               state=0;
               count=(count+1) % 4;
Now the 'key' to this, is that each loop, only does a very little work. The instruction to set the adc_channel, only takes a couple of uSec. Similarly, the 'ADC_START_ONLY' instruction, only requires triggering a single bit in the processor, while the 'ADC_READ_ONLY', makes no attempt to test if the value is ready, but simply loads the two bytes from the ADC registers. Since the routine is called every 250uSec, the sequence is actually:
Time Action
0 select the channel
250 start the ADC
500 read the ADC
750 advance the channel number
1000 select the channel....
This allows 250uSec for the ADC to settle, then 250 for the reading etc. etc., without wasting time at each stage. :-)
sraiderk
PostPosted: Fri Feb 25, 2005 5:06 am     Reply with quote
Thank you very much all person giving responce to my request.
The example sended by Ttelmah is perfect to me for understanding the ADC.