Calibrating an ADC
arunb
Calibrating an ADC
PostPosted: Mon Oct 18, 2004 8:39 am     Reply with quote
How can ADCs be calibrated ???
thanks
arun
Re: Calibrating an ADC
PostPosted: Mon Oct 18, 2004 9:35 am     Reply with quote
arunb wrote:
thanks
arun
Lots of different ways. You could read two 'known' voltages, and store the values, and use these to give a 'scale factor'. Alternatively, you could do it in hardware, by having Vref high and Vref low both adjustable, using a digital pot to adjust each voltage, then putting in your 'zero point' voltage, and adjusting the low Vref, till the correct 'low' reading is received (personally, I'd use '1', not '0' - this way you can tell if you ae below the zero reading). Then feed in the 'high point' voltage, and adjust the high Vref, till the correct reading is obtained.
John Morley
PostPosted: Mon Oct 18, 2004 9:24 pm     Reply with quote
I applied a couple of known voltages to the inputs of my A/D, and read the results. I then manually calculated the "scale factor" required to make the A/D readings agree with the known input, and hard-wired this factor into my code. Now, each time I read the A/D I apply the scale factor.
float fADCorrection = 0.975;   // empirically derived scale factor for A/D channels.
fVolts =(((float)iRawData/256)*15) * fADCorrection;
Fortunately, all channels had (roughly) the same scale factor, so I got away with only one value for all channels. Also, this technique only nulls "gain" errors, so if you have "offset" errors as well, you'll need to do more work. Fortunately, that was not really evident in my data collection.
Good Luck!
John Morley
arunb
RE:
PostPosted: Mon Oct 18, 2004 9:53 pm     Reply with quote
Thank you for the reply.
I had something exactly similar in mind, but what I don't know is what should be values of the known voltages ??
Should I start with something as low as 50 mV and go up to 5 V ( or Vref value).
Also is the calibrating factor different for each known voltage value ??
thank you
arun
Neutone
PostPosted: Tue Oct 19, 2004 8:07 am     Reply with quote
arunb wrote:
thanks
arun
Start by sampeling the minimum and maximum input values. Then use a form of the formula for a line y=mx+b.
   Analog_Input_1_m=Analog_Input_1_High-Analog_Input_1_Low;
   Analog_Input_1_m=0x10000000/Analog_Input_1_m;
I use this arangement of the formula because it is least dificult to solve y=(x-b)*m
Analog_Input_1=((int32)(Analog_Input_1_RAW-Analog_Input_1_Low) * Analog_Input_1_m) >> 16;
