I am using interrupt to control external device
Goto page 1, 2  Next
maiprog
PostPosted: Tue Mar 25, 2014 7:01 am     Reply with quote
This is my code. I need to HIGH and LOW the pin_b2
so i need delay_us... my code is below:
#INT_RTCC
void inductor_firing_isr()
    if(enable_firing_interrupt == 1)
    output_high(PIN_B2);
    delay_us(20);
    output_low(PIN_B2);
    set_timer0(0);
    enable_firing_interrupt = 0;
Is their any way rather than using the delay in interrupts ?
PostPosted: Tue Mar 25, 2014 7:29 am     Reply with quote
yes, simply set a flag within the ISR then in main(), test that 'flag' and if set, do what you want with pin_b2.
You want ISRs to be small and fast, so NO delays, printf(), or math just simple set/clr flags.
hth
jay
PostPosted: Tue Mar 25, 2014 7:48 am     Reply with quote
Timer 0 will be set to zero when the interrupt is taken.
Therefore you can look for a small count greater than zero as your delay,
based on the timer prescalar- master clock etc...
If latency for the pulse you make is critical after the int - then you will have to do it in the isr.
None of this gets around the question of ISR time hogging.
If you have no other foreground or overlapped #int handlers
that could be the alternative to using the ugly delay_us().
Without knowing the PIC - i don't know if you are reading an 8 or 16 bit register for the timer though.
# define mydelay 7
#INT_RTCC
    while(get_timer0()<mydelay){};
    output_low(PIN_B2);
    set_timer0(0);
maiprog
PostPosted: Tue Mar 25, 2014 9:07 am     Reply with quote
I am using pic18f4520 and int8
maiprog
PostPosted: Tue Mar 25, 2014 9:08 am     Reply with quote
Why mydelay 7, any reason for that
jeremiah
PostPosted: Tue Mar 25, 2014 10:49 am     Reply with quote
Because if you put the delay in the ISR, then any delays in your main code could cause interrupts to be disabled (depends on if the compiler inlines the delay or not).
Without knowing much about your hardware situations, some other thoughts:
If your clock is fast enough, you could do a small conditional in your ISR:
#INT_RTCC
   static BOOLEAN pulse = FALSE;
   if(enable_firing_interrupt){
      if(!pulse)
         set_timer0(250);  //pick a value here that makes the interrupt happen 20us later
         pulse = TRUE;
      }else{
         output_low(PIN_B2);
         set_timer0(0);
         pulse = FALSE;
         enable_firing_interrupt = FALSE;
In this scenario, when you set enable_firing_interrupt to TRUE, the first IF happens setting the line high and the interrupt finishes. The set_timer0() call in the IF section should be selected to account for the time it takes for the interrupt to save registers, etc. The next time the interrupt fires, it goes to the ELSE section, which brings the line low and disables the section.
maiprog
PostPosted: Tue Mar 25, 2014 12:47 pm     Reply with quote
K, and i am too getting errors such as:
interrupt disabled call to prevent re-entrancy:[lcd_send_nibble], [lcd_send_nibble] ,
[@mulff],[@delay_ms1] and [synchronize_on_rising_edge]
How to eliminate these errors ?
PostPosted: Tue Mar 25, 2014 1:33 pm     Reply with quote
You should have posted your entire program, not just the ISR, as I can see those 'errors' come from an LCD function or routine NOT in your original post.
You must understand that the PIC once in a delay function can not be called a second time.Usually you'll get this error with delay code inside an ISR.
If you post your entire code,others can better comment on what's going on....how to fix..
hth
jay
jeremiah
PostPosted: Tue Mar 25, 2014 4:13 pm     Reply with quote
This not an error, it is a warning. However, you do need to pay attention to them. It says that you are using functions in your ISR (delay_ms, lcd_send_nibble. synchronize_on_rising_edge) and in your main code. You really should avoid doing this. It means that you cannot fire interrupts while these functions run because of how you placed them in the code. Avoid using ms delays or LCD functions or Floating point operations in your ISR. It can cause a lot of problems for you.
maiprog
PostPosted: Wed Mar 26, 2014 12:30 am     Reply with quote
This is my code....
and i am using the LCD.c inbuilt driver of ccs compiler.
#include <18f4520.h>
//#fuses HS, NOWDT, NOPROTECT, NOPUT, NOBROWNOUT
#FUSES HS                       //High speed Osc (> 4mhz)
#FUSES BORV25                   //Brownout reset at 2.5V
#FUSES NOPUT                    //No Power Up Timer
#FUSES LVP                      //Low Voltage Programming on B3(PIC16) or B5(PIC18)
#FUSES PBADEN                   //PORTB pins are configured as analog input channels on RESET
#FUSES NOEBTRB                  //Boot block not protected from table reads
#FUSES NOCPB                    //No Boot Block code protection
#FUSES NOLPT1OSC                //Timer1 configured for higher power operation
#FUSES MCLR                     //Master Clear pin enabled
//#FUSES XINST                    //Extended set extension and Indexed Addressing mode enabled
#use delay(clock=25M)
#include <LCD.C>
//#use standard_io(a)
//#use standard_io(b)
#zero_ram
#define ON 1
#define OFF 0
#define NUM_CAP_BANKS 3
#define TCR_LIMIT 10
#define LEADING_LIMIT -28
#define TURN_ON -1
// Unsigned INT (8 bit):   0   -> +256
// Signed INT (8 bit):   -128 -> +128
// CCS Compiler makes INTs unsigned by default
//Fuzzy System
//Input Membership Function
//                                -20  -15  -10   -5   0    5   10  15  20  25
signed int PhaseAngle_Input[10] = {40,  45,  50,  55,  60,  65, 70, 75, 80, 85};
//Output Membership Function
//                                           91  95  100  112  115  122  124  126 128 135
unsigned int FiringAngleChange_Output[10] = {1,  5,  10,  22,  25,  32,  34,  36, 38, 45};
//Fuzzy TSK Rules
unsigned int Rules[10] = {0, 1, 2, 3, 4, 5, 5, 7, 8, 9};
// One Input - One Output Fuzzy Function Prototype
unsigned int fuzzy_tsk(float);
//General Prototypes
void turn_capacitors_on();
void turn_capacitors_off();
void turn_inductor_on();
void turn_inductor_off();
signed long int round(float x);
void synchronize_on_rising_edge();
//Globals - little necessary
signed long ticks = 0;
//short int look_for_voltage = 1;
float phase_angle = 0.0;
unsigned long int firing_angle = 90;
short int voltage_state = 0;
short int current_state = 0;
short int bLagging = 0;
short int voltage_initial_state = 0;
short int current_initial_state = 0;
short int enable_firing_interrupt = 0;
float time_delay = -1.0;
int counter_set = 0;
signed long int interrupt_counter = 0;
/* Perform Capacitor Bank TSC Initialization Here */
int capacitor_banks[NUM_CAP_BANKS];
/* TSC Capacitor Bank Prototypes */
void set_capacitor_banks(void);
void control_capacitor_banks(int, int );
void turn_on_all_capacitor_banks(void);
void turn_off_all_capacitor_banks();
int find_number_of_cap_banks_on(void);
/* TCR Interrupt */
#INT_RTCC
    delay_us(20);
    output_low(PIN_B2);
    set_timer0(0);
/* LCD Interrupt */
#INT_TIMER2
void timer_2_isr()
    interrupt_counter++;
    if(interrupt_counter >= 100)
       interrupt_counter=0;
       printf(LCD_putc,"\f%3.2f",phase_angle);
       lcd_gotoxy(0,1);
       printf(LCD_putc, "FA: %ld", firing_angle);
       lcd_gotoxy(0,2);
       printf(LCD_putc, "Cap: %d", find_number_of_cap_banks_on());
       //Synchronize Voltage Since Cycles Missed
/* Main mSVC Code */
    signed long int capacitor_counter = TURN_ON;
    //Set the LCD
    //Set Up Timer 0
    set_rtcc(0);
    setup_counters(RTCC_INTERNAL, RTCC_DIV_128);
    enable_interrupts(INT_RTCC);
    //Set Up Timer 2
    set_timer2(0);
    setup_timer_2(T2_DIV_BY_16, 0xFF, 16);
    //Turn On All Interrupts
    //Set up timer 1
    set_timer1(0);
    setup_timer_1( T1_INTERNAL | T1_DIV_BY_4);
    setup_timer_1( T1_INTERNAL | T1_DIV_BY_8);
    //Initialize Capacitor Banks to Off
//    turn_off_all_capacitor_banks();
    //Main While Loop Controls PSVC
     while(ON)
//Turn Off the LCD
 disable_interrupts(INT_TIMER2);
  //Update Capacitor Banks Once Every 5 Seconds
  if(capacitor_counter > 300 || capacitor_counter == TURN_ON)
  //Reset Capacitor Counter
     capacitor_counter = 0;
  //Set Capacitor Banks Based On Previous phase_angle
   set_capacitor_banks();
//Increment Capacitor Counter
 capacitor_counter++;
  //Continue Controlling mSVC
 //Determine Leading/Lagging
  voltage_state = input(PIN_A0);
  voltage_initial_state = voltage_state;
  while(voltage_initial_state == voltage_state)
  //Start Inductor Countdown as Voltage Crosses Zero
  if(time_delay != -1.0)
  set_timer0(counter_set);
  enable_firing_interrupt = 1;
  //Take Current Reading
  current_state = input(PIN_A1);
  //Going from L->H
  if((voltage_initial_state == 0) && (voltage_state == 1))
  if(current_state == 0)
   bLagging = 1;
   bLagging = 0;
  //Going from H->L
  else if((voltage_initial_state == 1) && (voltage_state == 0))
   bLagging = 0;
   bLagging = 1;
  if(bLagging == 1)
  //Read Voltage First
    //Wait for Voltage Zero Crossing
  while(voltage_state == input(PIN_A0))
  set_timer1(0);
//Read Current
    //Wait for Current Zero Crossing
  while(current_state ==  input(PIN_A1))
  ticks = get_timer1();
  //Read Current  First
  //Set the Timer
  set_timer1(0);
  //Read Voltage
  ticks = -ticks;
  //Calculate Phase Angle from Ticks Counted
  phase_angle = ( ((float)ticks * (float)0.0000016) / (1.0 / 60.0)) * 360.0;
//Account for Rollover
  if((phase_angle <= -170.0) && (phase_angle >= -180.0 ))
    phase_angle = -(180.0 + phase_angle);
//Weed out False Signals
  if((phase_angle > -50.0) && (phase_angle < 130.0))
  //Ensure Lower Bound is Met
  if(phase_angle <=  -20)
   phase_angle = -19;
  if( phase_angle > -55 && phase_angle < 55 )
   //Invoke Fuzzy System
      //Fuzzy System Returns Updated Firing Angle
   firing_angle = fuzzy_tsk(phase_angle);
      //Convert Desired Firing Angle to a Delay Time
      time_delay = (((float)firing_angle / 360.0) * (1.0 / 60.0));
      counter_set = round(time_delay / 0.0000256);
      counter_set = 255 - counter_set;
    //Show the Phase on LCD
//Set Number of Capacitor Banks
void set_capacitor_banks()
    int i=0;
    //Check if Phase is Lagging - Only Add More Capacitors
    //If Phase Is Lagging
    if (phase_angle > 0)
  //Only Add More Capacitors If Phase > TCR_LIMIT Degrees
  //10 Degrees Is the Current Span of the TCR Branch
  if (phase_angle > TCR_LIMIT)
    //Add the Next Available Capacitor Bank
    for(i=0; i<NUM_CAP_BANKS; i++)
   if (capacitor_banks[i] == OFF)
    //Turn On Capacitor Bank
    control_capacitor_banks(i,ON);
    //Remove a Capacitor Bank If Leading Too Much
    else if (phase_angle < LEADING_LIMIT)
  for(i=NUM_CAP_BANKS-1; i>=0; i--)
    if (capacitor_banks[i] == ON)
       //Turn Off Capacitor Bank
   control_capacitor_banks(i,OFF);
//Returns the Number Of Capacitor Banks On
   int i=0;
   int banks_turned_on = 0;
           banks_turned_on++;
   return (banks_turned_on);
//Control Capacitor Banks
//Individual PIC Pins Needed
void control_capacitor_banks(int bank, int mode)
//Wait for Current to Cross Zero Before Switching Capacitor
  current_initial_state = current_state;
  while(current_initial_state == current_state)
  //1st Capacitor Bank
  if (bank == 0)
    if (mode == OFF)
        output_low(PIN_B1);
        capacitor_banks[bank] = OFF;
        output_high(PIN_B1);
        capacitor_banks[bank] = ON;
  //2nd Capacitor Bank
  else if (bank == 1)
    if (mode == OFF)
        output_low(PIN_B3);
        output_high(PIN_B3);
  //3rd Capacitor Bank
        else if (bank == 2)
    if (mode == OFF)
        output_low(PIN_A2);
        output_high(PIN_A2);
//Synchronize on Rising Edge of Voltage
    //Wait for Voltage to Change State
    //Going from L->H
  bLagging = 1;
  bLagging = 0;
  //Going from H->L
  bLagging = 0;
  bLagging = 1;
//Wait for Rising Edge of Voltage
 if(bLagging == 1)
  if(input(PIN_A0) == 0)
  while(input(PIN_A0) ==  0)
    //Just Wait for Voltage to Go from H->L
  if(input(PIN_A1) == 0)
  while(input(PIN_A1) ==  0)
    //Just Wait for Current to Go from H->L
//Rounding Function on a Float
    //float decimal = 0.0;  //Commented to Save RAM
    int return_rounded = 0;
    if((x - ((signed long int)x)) < 0.5)
        return_rounded = ((signed long int)x);  //This is the floor function
  return_rounded = ((signed long int)(x+1));  //This is the ceil function
    return (return_rounded);
//One input-output TSK Fuzzy Engine
unsigned int fuzzy_tsk(float crisp_in)
   float fired[2] = {0,0};
   int rules[2] = {0,0};
   unsigned int out = 0;
   signed int a = 0;
   signed int b = 0;
   signed int c = 0;
   signed int d = 0;
   signed int e = 0;
   signed int f = 0;
   signed int g = 0;
   signed int h = 0;
   signed int i = 0;
   signed int j = 0;
   a = PhaseAngle_Input[0];  // -40
   b = PhaseAngle_Input[1];  // -30
   c = PhaseAngle_Input[2];  // -12
   d = PhaseAngle_Input[3];  // -5
   e = PhaseAngle_Input[4];  // 0
   f = PhaseAngle_Input[5];  // 5
   g = PhaseAngle_Input[6];  // 12
   h = PhaseAngle_Input[7];  // 30
   i = PhaseAngle_Input[8];  // 40
   j = PhaseAngle_Input[9];
   //Scale to Fit Fuzzy Rules
   crisp_in += 60.0;
   //Start Fuzzy TSK
   if ((crisp_in >= a) && (crisp_in < b))
         fired[0] = (-1.0) * ( crisp_in / (float)a ) + 1.0;
    rules[0] = 0;
    rules[1] = 1;
   else if ((crisp_in >= b) && (crisp_in < c))
    fired[0] = ((-1.0 )* crisp_in + (float)c) /((float)(c-b));
    rules[0] = 1;
    rules[1] = 2;
   else if ((crisp_in >= c) && (crisp_in < d))
    fired[0] = ((-1.0)* crisp_in + (float)d) / ((float)(d-c));
    rules[0] = 2;
    rules[1] = 3;
   else if ((crisp_in >= d) && (crisp_in < e))
    fired[0] = ((-1.0)* crisp_in+ (float)e) / ((float)(e-d));
    rules[0] = 3;
    rules[1] = 4;
   else if ((crisp_in >= e) && (crisp_in < f))
    fired[0] = ((-1.0)* crisp_in + (float)f) / ((float)(f-e));
    rules[0] = 4;
    rules[1] = 5;
   else if ((crisp_in >= f) && (crisp_in < g))
    fired[0] = ((-1.0)*crisp_in+ (float)g) / ((float)(g-f));
    rules[0] = 5;
    rules[1] = 6;
   else if ((crisp_in >= g) && (crisp_in < h))
    fired[0] = ((-1.0)*crisp_in+(float)h) / ((float)(h-g));
    rules[0] = 6;
    rules[1] = 7;
       rules[0] = 7;
       rules[1] = 8;
   fired[1] = 1 - fired[0];
 out = (unsigned int)(FiringAngleChange_Output[Rules[rules[0]]]*fired[0] +
FiringAngleChange_Output[Rules[rules[1]]]*fired[1]);
  // Scale Firing Angle from Fuzzy Rules
   out += 90;
   return out;
jeremiah
PostPosted: Wed Mar 26, 2014 6:45 am     Reply with quote
The timer interrupt is your issue. Printing to the LCD and also calling find_number_of_cap_banks_on() will cause most if not all those. It's not a very safe or stable design. Your timer will prevent your other interrupt from firing and causes the disabling of interrupts in the main.
A better approach would be to set a flag in the ISR and handle monitoring that flag in your main, updating as you are able.
PostPosted: Wed Mar 26, 2014 7:40 am     Reply with quote
These two fuse settings are wrong and can cause a lot of headaches!
99% of programmers do NOT use LVP. so select NOLVP
commenting out the XINST does not necessarily select NOXINST.
You're always best to configure them yourself, do not rely on 'wizards' or 'defaults'. With PICs having more fuses and instructions , always confirm from the listing what the fuses really are.Even compiler versions might change them as well...
Interesting to see 'fuzzy' logic ! I thought it dies 2 decades ago !
hth
jay
PostPosted: Wed Mar 26, 2014 12:48 pm     Reply with quote
there are a number of other time wasting features in the program. this one jumped out at me:
rather than a floating point test -it would be simpler to do the test ONCE when you assign a new value to time_delay and use a flag such as :
int1 TDnot1
then you are setting it to zero or one as the present assignment of time_delay might require.
testing IT repeatedly uses VERY few precious clock cycles
PostPosted: Wed Mar 26, 2014 1:21 pm     Reply with quote
floats in general are a HUGE waste of time and processing power..
also printf()s inside ISRs is very,very bad programming.
jay
PostPosted: Wed Mar 26, 2014 1:48 pm     Reply with quote
let me reinforce what Jay means :
phase_angle need not be a float, since it's underlying "value" is derived from less than half of timer 1's register maximum and after more tedious floating point math to get to be "degrees" -minus your error limit test -the working resolution is less than 16000 counts of timer1!!!
ie: the BEST resolution of the 'float' you are likely to get is one part is
about 16000
using your own phase_angle integer coordinate space could be done with a signed int16 and the math would be so MUCH faster ..
THAT could be converted if need be when it changes for LCD display..
as a rule ONLY use floats when the precision of integers won't do.
HINT: 16 bit signed is all you need for your app!
in your case- INTeger math could do it all, even the LCD display with a bit of creativity .
Goto page 1, 2  Next