arunb
Is this code for page read write to 24LC512 EEPROM correct ? |
Posted: Mon Nov 11, 2013 8:59 am |
I am trying to develop page read and write functions for the 24LC512 EEPROM. The EEPROM is i2c based.
My code is given below.
devaddress=0xA0;
int nMMCBuffer[512];
//reads 512 bytes from the EERPROM
void pageread_ext_eeprom(int devaddrs,long int address){
int16 bytecntr;
//device address
bit_clear(devaddrs,0);
i2c_start();
i2c_write(devaddrs);
i2c_write(address>>8);
i2c_write(address);
i2c_start();
//read mode
bit_set(devaddrs,0);
//read in the data
bytecntr=0;
for (bytecntr=0;bytecntr<=511;bytecntr++){
nMMCBuffer[bytecntr]=i2c_read(1);
bytecntr++;
//no acknowledge, stops transfer
i2c_read(0);
i2c_stop();
//writes 512 bytes of data to the eeprom
void pagewrite_ext_eeprom(int devaddrs,long int address){
int16 bytecntr;
int pgcnt,i;
short int status;
i2c_start();
i2c_write(address);
bytecntr=0;
for (pgcnt=0;pgcnt<4;pgcnt++){
//transfer 128 bytes to on-chip page buffer
for (i=0;i<=127;i++){
i2c_write(nMMCBuffer[bytecntr]);
bytecntr++;
//transfers data from page buffer to EEPROM (actual write)
i2c_stop();
//poll for status of write
i2c_start();
status=i2c_write(devaddrs);
while(status==1)
i2c_start();
i2c_stop();
I just want an opinion, I have not tried this yet I will do so tomorrow.
thanks
a |
Posted: Mon Nov 11, 2013 10:21 am |
Several little comments.
Your read code, physically sets the low bit of devaddress. Means it won't work a second time, nor will the write, since the address is now set to 'read'...
Better to use:
#define READ 1
//Then to select read mode:
//read mode
i2c_write(devaddrs | READ);
This way the physical address is never changed.
Then you'll have a problem if the ROM address given to the functions, is not the start of a page.... Need to test for this.
I'd suggest you don't do the extra read to stop the transaction, but instead include this in the read:
//read in the data
for (bytecntr=0;bytecntr<=510;){
nMMCBuffer[bytecntr++]=i2c_read(1);
nMMCBuffer[bytecntr]= i2c_read(0); //last read stops the transfer
i2c_stop();
You are incrementing the counter twice in the loop, and clearing it twice before starting....
arunb
RE: |
Posted: Mon Nov 11, 2013 11:40 am |
Thanks, I didn't see those errors...
The ROM address is addressed like this.
address=512*Index
Index =0,1,2...n
so address will be= 0, 512, 1024 etc...
Do you think this will avoid the page boundaries...??
thanks
a |
Posted: Mon Nov 11, 2013 2:34 pm |
Looks good.
Why not make the functions just take the index then?.
