ADC_Value vs o\p display on 16*2 LCD
Goto page 1, 2  Next
sahu77
PostPosted: Sun Jan 01, 2012 12:19 pm     Reply with quote
Now I'm using like this:
/*        16F676 Configuration
          O = Output, I = Input
                                                      2.2K
                    _________   |-----------------^^^--
              Vdd   | 1  14 |  Vss                     | 4.7K
  (O)  L1 <-- RA5   | 2  13 |  AN0 <-- I\P V_Sense (I)--^^^--<|-- up to 15 V AC
  (O)  L2 <-- RA4   | 3  12 |  AN1 <-- O\P Volt_Sense (I)   1N4007
  (I) SW1 --> MCLR  | 4  11 |  RA2 --> NC  (O)
  (O) RS  <-- RC5   | 5  10 |  RC0 --> DB4 (O)
  (O)  E  <-- RC4   | 6   9 |  RC1 --> DB5 (O)
  (O) DB7 <-- RC3   | 7   8 |  RC2 --> DB6 (O)
  Function ProcessMains
  Reads ADC_Value and etc
int ProcessMains(void)
   set_adc_channel(0); // Select AN0
      delay_ms(ADC_DELAY);          //Charge capacitor
         read_adc(ADC_START_ONLY);       //Do A/D conversion
         done == adc_done();
         while(!done) {
            done = adc_done();
         temp_result += read_adc();          // Read A/D register .  Pin A0 in an input
      delay_ms(ADC_2TAD);               // Wait 2 TADs before doing another A/D conversion
   ADC_Value = temp_result / ADC_AVERAGE_COUNT;
   tlong = (int32)ADC_Value*500;    //Convert the result in millivolts
   tlong = tlong/1023;              // 0..1023 -> 0-5000mV
   volt = tlong;              // Extract volts (thousands of millivolts 250mv = 250volt
 lcd_init();
     lcd_putc("\fVOLT =volt \n");
     lcd_putc("I\P Volt");
Now anybody clear me, Value volt which display on 16*2 LCD are RMS VALUE or peak to peak VALUE?
sahu
asmboy
PostPosted: Sun Jan 01, 2012 12:33 pm     Reply with quote
up to 15 V AC
is that for real??? up to 15v AC thru a 4.7 k resistor ??
how are you expecting the PIC to deal with that signal?
sahu77
PostPosted: Sun Jan 01, 2012 12:53 pm     Reply with quote
asmboy wrote:
up to 15 V AC
yes its real via step down tx.
pls right now ignore any hardware mistake.
clear me only ---
sahu
SherpaDoug
PostPosted: Sun Jan 01, 2012 3:46 pm     Reply with quote
You will get the instantaneous voltage at the time the A/D samples. If you synchronize your A/D readings with the AC cycle you can get Peak readings. If you get the + peak and the - peak you can calculate the peak to peak value. To synchronize the PIC you usually use a "Zero Crossing Detector" circuit.
To get RMS you need to take many samples each cycle, then Square them, calculate the Mean over some time period, then take the square Root.
Note that the PIC A/D can not read negative instantaneous voltages. Your 4.7K & 2.2K divider will scale the positive voltages, but the negative ones will read as zero. As shown the negative 15 AC cycle would put 3mA into the PIC protection diode which is not a good idea.
sahu77
PostPosted: Mon Jan 02, 2012 10:54 am     Reply with quote
Please anybody sages me- how I can find true RMS value ?
sahu
PostPosted: Mon Jan 02, 2012 11:18 am     Reply with quote
SherpaDoug has very nicely explained the procedure for you.
Since only you control the design/build of the hardware, it's up to you to create the code you need. We can only offer limited help, not actual code as what we create will only work on our equipment.
sahu77
PostPosted: Mon Jan 02, 2012 12:46 pm     Reply with quote
oho oho no sir not need me complete code . need only
correction for this code
         done == adc_done();
         while(!done) {
            done = adc_done();
which give Mean OR RMS VALUE .
sorry my bad English
sahu
PostPosted: Mon Jan 02, 2012 12:50 pm     Reply with quote
ADC_value is already an average or mean value.
from your code...
You cannot get RMS value as you are not sampling the input AC voltage correctly. You MUST do all of what SherpaDoug has said before if you want RMS value.
Five easy steps to sucess.
SherpaDoug
PostPosted: Mon Jan 02, 2012 5:23 pm     Reply with quote
To get RMS (Root of the Mean Square) you must square the values BEFORE you average them. How long you average for depends on how fast a response you need versus noise immunity. You also want to average over complete cycles. Many meters that measure 50 or 60Hz use 100ms. That is 5 complete cycles at 50Hz or 6 at 60Hz. Then you take the square root.
Of course you will also have to alter your hardware to accurately read the negative half of the AC cycle.
sahu77
PostPosted: Sat Jan 07, 2012 9:41 am     Reply with quote
now today i found 1 new problem ....
problem as
  lcd_init();
      lcd_putc("\fVOLT = volt \n");
volt is a numeric ,but lcd display volt word .
I'm use flex_lcd.c as lcd driver .
now clear me where i wrong ?
sahu
PostPosted: Sat Jan 07, 2012 10:08 am     Reply with quote
Read a book on C?.....
You are sending the string 'VOLT = volt', which is what will be displayed.....
Look in the printf manual, in particular at the '%' operator, and it's formats.
sahu77
PostPosted: Sat Jan 07, 2012 10:17 am     Reply with quote
it is right
 LCD_PutChar("INPUT= "%ld ",volt");
sahu
PostPosted: Sat Jan 07, 2012 10:56 am     Reply with quote
While your project is open, press F11 to access the CCS C Onscreen HELP files !!
OR
LOOK at any of the examples that CCS kindly supplies to SHOW you HOW to use this compiler.
What you need to know is given there.
sahu77
PostPosted: Sat Jan 07, 2012 11:01 am     Reply with quote
i was also try it but not found my ans .
sahu
dyeatman
PostPosted: Sat Jan 07, 2012 12:22 pm     Reply with quote
You should be using lcd_putc in a printf statement.
The CCS Example file EX_LCDTH.C shows how it should be done..
There is another example in the current manual on page 216 under printf
Google and Forum Search are some of your best tools!!!!
Goto page 1, 2  Next
Page 1 of 2
